11G wrong IPMI data
Matt Domsch
Matt_Domsch at dell.com
Mon Jul 13 22:44:32 CDT 2009
On Fri, Jul 10, 2009 at 10:40:24AM +0200, Patrick Schreurs wrote:
> Hello,
>
> I'm struggling with temperature monitoring on a Dell R710. IPMI reports
> a sensor as critical. We several R170's in a professional cool
> datacenter. They all report the same critial:
>
> ~# ipmitool sdr|grep cr
> Temp | 53 degrees C | cr
>
> The ambient temperature of this server is 17 degrees (celsius). Dell
> advices to adjust the datacenter's climate, which isn't very helpful.
At some point, the specification for these values changed. Instead of
being an actual $temperature_now, the value means "delta between
$temperature_now and $temperature_fail", e.g. the amount of safety
room you have before you hit the critical point.
--
Matt Domsch
Technology Strategist, Dell Office of the CTO